On 16/03/2025 15:37, Tricky Dicky wrote:
My heating system has reported that one of the TRVs is not fully shutting
off and I have found the radiator getting warm when it should be off. I
have carried out the recommended service of moving the stem and adding some silicone lubricant. My question is how much movement should there be in the valve stem it protrudes approximately 3mm above the valve and there is
about 2mm of movement, is this normal or am I looking at replacing the
valve body?
Richard
That sounds like about a normal movement. Have you got a decorators cap
that you can put on it in place of the head? If so does that keep the
radiator cold? Are you sure that you have installed the head on the body correctly? Put the temperature to the highest setting, fully undo the
retaining screw ring, push down on the head to firmly to seat the head
on the body before doing up the retaining screw ring.
--