First time yesterday and again today. I was sitting around for an hour yesterday thinking it was a power cut, but investigation showed it was a
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many times yesterday without incident.
jon <[email protected]> wrote:
First time yesterday and again today. I was sitting around for an hour
yesterday thinking it was a power cut, but investigation showed it was a
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many
times yesterday without incident.
It could be many things, in two senses.
It could be that you have 'many things' each of which is adding a
little leakage and that adding just one more has been "the straw that
breaks the camel's back". One particular type of 'thing' that can do
this is PCs. Have you several PCs running?
The other type of 'many things' is simply that it could simply be one
thing which has slowly deteriorated and is now tripping the RCD
occasionally. A common culprit for this is an oven element.
On 17/01/2025 09:30, Chris Green wrote:
jon <[email protected]> wrote:
First time yesterday and again today. I was sitting around for an hour
yesterday thinking it was a power cut, but investigation showed it was a >>> trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many >>> times yesterday without incident.
It could be many things, in two senses.
It could be that you have 'many things' each of which is adding a
little leakage and that adding just one more has been "the straw that
breaks the camel's back". One particular type of 'thing' that can do
this is PCs. Have you several PCs running?
I'll second that.
At one point, we had a home server and up to 5 PCs, plus 3 printers, 3 >satellite boxes, two digital terrestrial boxes and God knows what else >running - much less now two of the kids are away at university - and we >suffered random trips. I got rid of the RCD and replaced all the
breakers with RCBOs, thus spreading the device leakage across different >circuits, and we've had no problem since.
The other type of 'many things' is simply that it could simply be one
thing which has slowly deteriorated and is now tripping the RCD
occasionally. A common culprit for this is an oven element.
Washing machine or dishwasher elements are also a likely culprit too.
First time yesterday and again today. I was sitting around for an hour yesterday thinking it was a power cut, but investigation showed it was aFirst disconnect the neutrals one by one off the consumer unit and test
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many times yesterday without incident.
On 17/01/2025 06:11, jon wrote:
First time yesterday and again today. I was sitting around for an hourFirst disconnect the neutrals one by one off the consumer unit and test
yesterday thinking it was a power cut, but investigation showed it was a
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many
times yesterday without incident.
for shorts to ground, with and without appliances connected
First time yesterday and again today. I was sitting around for an hour yesterday thinking it was a power cut, but investigation showed it was a
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many times yesterday without incident.
On 17/01/2025 10:11, RJH wrote:
On 17 Jan 2025 at 10:04:47 GMT, The Natural Philosopher wrote:
On 17/01/2025 06:11, jon wrote:
First time yesterday and again today. I was sitting around for an hour >>> yesterday thinking it was a power cut, but investigation showed it was a >>> trip of the main breaker.First disconnect the neutrals one by one off the consumer unit and test
I have noticed the breaker is very hard to reset, very stiff to change >>> switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many >>> times yesterday without incident.
for shorts to ground, with and without appliances connected
OOI, how do you go about isolating the supply, before the CU? I've recently had the switch/breaker replaced with a 100A fuse protected with a seal.
I'd have to break the seal to isolate the CU, leaving the only way to isolate
to any extent is at the CU.
The CU's main switch will isolate the supply to everything else in the
box. You're not looking at disconnecting the supply tails, so you don't
need to isolate before the switch.
On 17 Jan 2025 at 10:04:47 GMT, The Natural Philosopher wrote:
On 17/01/2025 06:11, jon wrote:
First time yesterday and again today. I was sitting around for an hourFirst disconnect the neutrals one by one off the consumer unit and test
yesterday thinking it was a power cut, but investigation showed it was a >>> trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many >>> times yesterday without incident.
for shorts to ground, with and without appliances connected
OOI, how do you go about isolating the supply, before the CU?
had the switch/breaker replaced with a 100A fuse protected with a seal.
I'd have to break the seal to isolate the CU, leaving the only way to isolate to any extent is at the CU.
On 17 Jan 2025 at 10:04:47 GMT, The Natural Philosopher wrote:
On 17/01/2025 06:11, jon wrote:
First time yesterday and again today. I was sitting around for an hourFirst disconnect the neutrals one by one off the consumer unit and test
yesterday thinking it was a power cut, but investigation showed it was a >>> trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many >>> times yesterday without incident.
for shorts to ground, with and without appliances connected
OOI, how do you go about isolating the supply, before the CU? I've recently had the switch/breaker replaced with a 100A fuse protected with a seal.
I'd have to break the seal to isolate the CU, leaving the only way to isolate to any extent is at the CU.
jon wrote:
First time yesterday and again today. I was sitting around for an hourBy "main breaker" do you mean the breaker between the meter and the CU,
yesterday thinking it was a power cut, but investigation showed it was a
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many
times yesterday without incident.
or something inside the CU? If inside, is it an MCB or an RCD/RCBO?
(In case you aren't aware, an RCD or RCBO will have a test button and an
MCB will not.)
jon <[email protected]> wrote:
First time yesterday and again today. I was sitting around for an hour
yesterday thinking it was a power cut, but investigation showed it was
a trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle
many times yesterday without incident.
It could be many things, in two senses.
It could be that you have 'many things' each of which is adding a little leakage and that adding just one more has been "the straw that breaks
the camel's back". One particular type of 'thing' that can do this is
PCs. Have you several PCs running?
The other type of 'many things' is simply that it could simply be one
thing which has slowly deteriorated and is now tripping the RCD
occasionally. A common culprit for this is an oven element.
It can of course also be a wiring fault where some insualation has worn
or a junction box has got water in it but these are relatively rarer (at least in my experience).
The breaker being "very hard to reset" isn't significant I don't think.
If repeatedly tripped my experience is that some RCDs get paranoid and
trip again even though the main leakage culprit has been removed.
Usually however, if this happens, just remove all the loads, reset the breaker and then turn circuits back on one by one. Of course if you
then get a trip when one of the circuits is turned back on you have a
good clue as to where the problem is.
All in all it can be quite difficult to find what is causing the trip
when it's a bit random (as you're seeing). If it's something like an
oven element failing then it almost always gets worse quite quickly and
is then easy to find. Otherwise you will just have to try and be as
logical as you can when trying to deduce where the problem is.
On Fri, 17 Jan 2025 09:30:29 +0000, Chris Green wrote:
jon <[email protected]> wrote:
First time yesterday and again today. I was sitting around for an hour
yesterday thinking it was a power cut, but investigation showed it was
a trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle
many times yesterday without incident.
It could be many things, in two senses.
It could be that you have 'many things' each of which is adding a little
leakage and that adding just one more has been "the straw that breaks
the camel's back". One particular type of 'thing' that can do this is
PCs. Have you several PCs running?
The other type of 'many things' is simply that it could simply be one
thing which has slowly deteriorated and is now tripping the RCD
occasionally. A common culprit for this is an oven element.
It can of course also be a wiring fault where some insualation has worn
or a junction box has got water in it but these are relatively rarer (at
least in my experience).
The breaker being "very hard to reset" isn't significant I don't think.
If repeatedly tripped my experience is that some RCDs get paranoid and
trip again even though the main leakage culprit has been removed.
Usually however, if this happens, just remove all the loads, reset the
breaker and then turn circuits back on one by one. Of course if you
then get a trip when one of the circuits is turned back on you have a
good clue as to where the problem is.
All in all it can be quite difficult to find what is causing the trip
when it's a bit random (as you're seeing). If it's something like an
oven element failing then it almost always gets worse quite quickly and
is then easy to find. Otherwise you will just have to try and be as
logical as you can when trying to deduce where the problem is.
Only one PC running at the moment.
First time yesterday and again today. I was sitting around for an hour yesterday thinking it was a power cut, but investigation showed it was a
trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many times yesterday without incident.
SteveW <[email protected]> wrote:
On 17/01/2025 10:11, RJH wrote:
On 17 Jan 2025 at 10:04:47 GMT, The Natural Philosopher wrote:
On 17/01/2025 06:11, jon wrote:
First time yesterday and again today. I was sitting around for an hour >>>>> yesterday thinking it was a power cut, but investigation showed it was a >>>>> trip of the main breaker.First disconnect the neutrals one by one off the consumer unit and test >>>> for shorts to ground, with and without appliances connected
I have noticed the breaker is very hard to reset, very stiff to change >>>>> switch position for reset. Not sure if that is a problem itself yet. >>>>>
I had a kettle on this morning when it tripped, but used the kettle many >>>>> times yesterday without incident.
OOI, how do you go about isolating the supply, before the CU? I've recently >>> had the switch/breaker replaced with a 100A fuse protected with a seal.
I'd have to break the seal to isolate the CU, leaving the only way to isolate
to any extent is at the CU.
The CU's main switch will isolate the supply to everything else in the
box. You're not looking at disconnecting the supply tails, so you don't
need to isolate before the switch.
Just be sure not to touch the upstream side of that switch. Ideally there should be protection on those terminals, but that doesn't seem to be
common practice. You could probably put some tape over the screws
to prevent mishaps, but it would be nicer if there was an official cover.
On 17 Jan 2025 at 10:04:47 GMT, The Natural Philosopher wrote:
On 17/01/2025 06:11, jon wrote:
First time yesterday and again today. I was sitting around for an hourFirst disconnect the neutrals one by one off the consumer unit and test
yesterday thinking it was a power cut, but investigation showed it was a >>> trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change
switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle many >>> times yesterday without incident.
for shorts to ground, with and without appliances connected
OOI, how do you go about isolating the supply, before the CU? I've recently had the switch/breaker replaced with a 100A fuse protected with a seal.
I'd have to break the seal to isolate the CU, leaving the only way to isolate to any extent is at the CU.
On 17/01/2025 12:23, jon wrote:
On Fri, 17 Jan 2025 09:30:29 +0000, Chris Green wrote:
jon <[email protected]> wrote:
First time yesterday and again today. I was sitting around for an hour >>>> yesterday thinking it was a power cut, but investigation showed it was >>>> a trip of the main breaker.
I have noticed the breaker is very hard to reset, very stiff to change >>>> switch position for reset. Not sure if that is a problem itself yet.
I had a kettle on this morning when it tripped, but used the kettle
many times yesterday without incident.
It could be many things, in two senses.
It could be that you have 'many things' each of which is adding a little >>> leakage and that adding just one more has been "the straw that breaks
the camel's back". One particular type of 'thing' that can do this is
PCs. Have you several PCs running?
The other type of 'many things' is simply that it could simply be one
thing which has slowly deteriorated and is now tripping the RCD
occasionally. A common culprit for this is an oven element.
It can of course also be a wiring fault where some insualation has worn
or a junction box has got water in it but these are relatively rarer (at >>> least in my experience).
The breaker being "very hard to reset" isn't significant I don't think.
If repeatedly tripped my experience is that some RCDs get paranoid and
trip again even though the main leakage culprit has been removed.
Usually however, if this happens, just remove all the loads, reset the
breaker and then turn circuits back on one by one. Of course if you
then get a trip when one of the circuits is turned back on you have a
good clue as to where the problem is.
All in all it can be quite difficult to find what is causing the trip
when it's a bit random (as you're seeing). If it's something like an
oven element failing then it almost always gets worse quite quickly and
is then easy to find. Otherwise you will just have to try and be as
logical as you can when trying to deduce where the problem is.
Only one PC running at the moment.
Unless they are unplugged or physically switched off (not the PC power button), the power input filters will still be connected to the mains
and they'll still contribute to the total leakage.
On 17/01/2025 10:11, RJH wrote:
I'd have to break the seal to isolate the CU, leaving the only way to
isolate to any extent is at the CU.
Fit a new seal?
Yes, it's that 'be sure' bit that makes me want to isolate away from the CU.
It's something I looked at because an electrician just quoted me nearly £500 to fit (and presumably check etc.) an additional MCB to the CU, and connect it
to existing cable.
On 17/01/2025 12:23, jon wrote:
On Fri, 17 Jan 2025 09:30:29 +0000, Chris Green wrote:
All in all it can be quite difficult to find what is causing the trip
when it's a bit random (as you're seeing). If it's something like an
oven element failing then it almost always gets worse quite quickly and
is then easy to find. Otherwise you will just have to try and be as
logical as you can when trying to deduce where the problem is.
Only one PC running at the moment.
Unless they are unplugged or physically switched off (not the PC power button), the power input filters will still be connected to the mains
and they'll still contribute to the total leakage.
| Sysop: | Keyop |
|---|---|
| Location: | Huddersfield, West Yorkshire, UK |
| Users: | 715 |
| Nodes: | 16 (2 / 14) |
| Uptime: | 15:32:08 |
| Calls: | 12,102 |
| Calls today: | 2 |
| Files: | 15,004 |
| Messages: | 6,518,049 |