• More Qs on generator

    From Ted Heise@21:1/5 to All on Sun Aug 11 12:39:34 2024
    Okay, last week I went to my local Harbor Freight and looked at
    the Predator 1600 that someone here (George?) suggested. It's a
    good bit lighter (and somewhat smaller) than their comparable 2000
    W unit, so that makes it attractive.

    Yesterday I got the details on the AC unit from the trailer, and
    posted it here...

    https://panix.com/~theise/AC-plate.jpg

    The part number on that brings up this page...

    https://colemanmachac.com/coleman-mach-15-ducted-48204-0690-quiet-black-1500btu/

    I don't think the unit has the optional heater. The stack of
    manuals I got with the trailer did have a sheet on installation of
    the heater accessory, but I haven't seen any evidence of one
    actually being operational.

    At any rate, I'm now wondering if the AC would run on the 1600 W
    generator. The spec for the compressor (12.9 A) gives 1420 W
    (amps times volts, right?), so that suggests maybe?

    On the other hand, the plate also shows 19.0 max circuit amperage
    (i.e., 2090 W), so that suggests even a 2000 W generator might not
    supply enough to run it.

    What advice do more experienced and knowledgeable folks here have
    for me?

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From sticks@21:1/5 to Ted Heise on Sun Aug 11 08:28:09 2024
    On 8/11/2024 7:39 AM, Ted Heise wrote:
    Okay, last week I went to my local Harbor Freight and looked at
    the Predator 1600 that someone here (George?) suggested. It's a
    good bit lighter (and somewhat smaller) than their comparable 2000
    W unit, so that makes it attractive.

    Yesterday I got the details on the AC unit from the trailer, and
    posted it here...

    https://panix.com/~theise/AC-plate.jpg

    The part number on that brings up this page...

    https://colemanmachac.com/coleman-mach-15-ducted-48204-0690-quiet-black-1500btu/

    I don't think the unit has the optional heater. The stack of
    manuals I got with the trailer did have a sheet on installation of
    the heater accessory, but I haven't seen any evidence of one
    actually being operational.

    At any rate, I'm now wondering if the AC would run on the 1600 W
    generator. The spec for the compressor (12.9 A) gives 1420 W
    (amps times volts, right?), so that suggests maybe?

    On the other hand, the plate also shows 19.0 max circuit amperage
    (i.e., 2090 W), so that suggests even a 2000 W generator might not
    supply enough to run it.

    What advice do more experienced and knowledgeable folks here have
    for me?

    I'd be very worried the smaller one would not be enough power. The big
    problem is the surge at startup. A couple days ago, I turned mine on
    and it actually went over 20 amps for a short period, and then stayed
    kinda high 17-18 amps draw for some time. Finally things settled down
    to the 11 amp draw noted previously.

    You might want to look at a soft start to mitigate the issue. They cost
    about $280, and I'm not sure how they manage to tone down the start
    capacitor, but I guess they do.

    <https://www.softstartrv.com/rvtravel/>

    It would be a bummer buying a compressor only to find out it won't run
    things for lack of power.



    --
    Stand With Israel!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From George Anthony@21:1/5 to Ted Heise on Sun Aug 11 20:02:58 2024
    On 8/11/2024 7:39 AM, Ted Heise wrote:
    Okay, last week I went to my local Harbor Freight and looked at
    the Predator 1600 that someone here (George?) suggested. It's a
    good bit lighter (and somewhat smaller) than their comparable 2000
    W unit, so that makes it attractive.

    Yesterday I got the details on the AC unit from the trailer, and
    posted it here...

    https://panix.com/~theise/AC-plate.jpg

    The part number on that brings up this page...

    https://colemanmachac.com/coleman-mach-15-ducted-48204-0690-quiet-black-1500btu/

    I don't think the unit has the optional heater. The stack of
    manuals I got with the trailer did have a sheet on installation of
    the heater accessory, but I haven't seen any evidence of one
    actually being operational.

    At any rate, I'm now wondering if the AC would run on the 1600 W
    generator. The spec for the compressor (12.9 A) gives 1420 W
    (amps times volts, right?), so that suggests maybe?

    On the other hand, the plate also shows 19.0 max circuit amperage
    (i.e., 2090 W), so that suggests even a 2000 W generator might not
    supply enough to run it.

    What advice do more experienced and knowledgeable folks here have
    for me?

    At the risk of sending you farther down the rabbit hole, look into a
    soft-start device for your AC. By the way, a good way to remember how to calculate wattage is "pie". Power equals amps (I) times volts (e).
    --
    “The Party told you to reject the evidence of your eyes and ears..."
    George Orwell

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to Ralph E Lindberg on Mon Aug 12 12:37:41 2024
    On Sun, 11 Aug 2024 07:38:58 -0700,
    Ralph E Lindberg <[email protected]> wrote:
    On 2024-08-11 12:39:34 +0000, Ted Heise said:

    Okay, last week I went to my local Harbor Freight and looked
    at the Predator 1600 that someone here (George?) suggested.
    It's a good bit lighter (and somewhat smaller) than their
    comparable 2000 W unit, so that makes it attractive.

    Yesterday I got the details on the AC unit from the trailer,
    and posted it here...

    https://panix.com/~theise/AC-plate.jpg

    The part number on that brings up this page...

    https://colemanmachac.com/coleman-mach-15-ducted-48204-0690-quiet-black-1500btu/


    I don't think the unit has the optional heater. The stack of
    manuals I got with the trailer did have a sheet on
    installation of the heater accessory, but I haven't seen any
    evidence of one actually being operational.

    At any rate, I'm now wondering if the AC would run on the 1600
    W generator. The spec for the compressor (12.9 A) gives 1420
    W (amps times volts, right?), so that suggests maybe?

    On the other hand, the plate also shows 19.0 max circuit
    amperage (i.e., 2090 W), so that suggests even a 2000 W
    generator might not supply enough to run it.

    What advice do more experienced and knowledgeable folks here
    have for me?

    No it will not.

    First the generators "rating" is peak power, so a 2KW (even
    Honda) only produces 1800 watts continuous
    Second the peak starting power of every A/C is the higher 19
    amp (unless you've added a "soft start" to the A/C)
    Third, there are other draws, like the converter and fridge.

    Generally -with- a soft start the min generator is 2200 watts,
    without 3KW (I prefer two ~2KW as I can carry them)

    Thanks, Ralph (and to George and sticks for similar advice).

    Regarding generator ratings, I've been checking both peak and
    static specs; for example, the Westinghouse unit I linked earlier
    is stated as 1800/2500, so I'd think that might do it.

    FWIW, I could run the fridge on propane, but am not sure what you
    mean by "convertor."

    In any case, I'm thinking I may just try that Westinghouse iGen
    2550DFc, and if it doesn't work then add a soft start.

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From sticks@21:1/5 to Ted Heise on Mon Aug 12 19:30:46 2024
    On 8/12/2024 7:37 AM, Ted Heise wrote:
    FWIW, I could run the fridge on propane, but am not sure what you
    mean by "convertor."

    Your unit has a "45 Amp Converter/Loadcenter" which I assume is what
    charges your house batteries when plugged into AC.

    --
    Stand With Israel!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From sticks@21:1/5 to Ted Heise on Tue Aug 13 16:52:59 2024
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    So here's an update. I went by Menard's yesterday just to look at
    what they had, and it just so happened that they had in stock the Westinghouse unit (and no others of similar capacity). Taking
    that as a sign it was meant to be, I went ahead and bought it.

    Now a bit of dumbassery. After adding oil and fuel, I could *not*
    get it to start--despite *many* yanks on the cord. I pulled the
    spark plug to see if I'd flooded it, but it seemed fine. Finally
    it occurred to me that the red light on the control panel might
    mean something. It was the oil light, and when I added more oil
    the unit started right up. In fairness, the dipstick goes in
    almost horizontally, so it's hard to read. Plus the manual had
    many warnings not to overfill.

    I took it to the trailer this afternoon, and it does indeed put
    out enough power to charge the battery. On the other hand, when I
    tried running the AC (with pretty much everything else off) the
    overload protection cut in. So I guess if I want to run the AC
    I'll need to try a soft start thingy.

    Yur makin' progress.
    Looking forward to finding out if the soft start works for you. I
    personally don't know anyone who uses one because of all having bigger generators.

    BTW, I can see where they (soft start) might come in handy at various
    camping joints. Some of them have 20/30 amp sites. Not sure exactly
    what they mean by that. I'm assuming the choice of either a regular 110
    volt 20 amp plug or the rounded 30 amp plug. I can see where lots of
    people need 110, but not a 30 amp service, so it makes sense. But, if
    the thing actually works, in a pinch you could stay at a site that only
    had the 20 amp service and still use it for your AC.


    --
    Stand With Israel!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to Ted Heise on Tue Aug 13 21:30:38 2024
    On Mon, 12 Aug 2024 12:37:41 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Sun, 11 Aug 2024 07:38:58 -0700,
    Ralph E Lindberg <[email protected]> wrote:
    On 2024-08-11 12:39:34 +0000, Ted Heise said:

    At any rate, I'm now wondering if the AC would run on the
    1600 W generator. The spec for the compressor (12.9 A)
    gives 1420 W (amps times volts, right?), so that suggests
    maybe?

    On the other hand, the plate also shows 19.0 max circuit
    amperage (i.e., 2090 W), so that suggests even a 2000 W
    generator might not supply enough to run it.

    What advice do more experienced and knowledgeable folks here
    have for me?

    No it will not.

    First the generators "rating" is peak power, so a 2KW (even
    Honda) only produces 1800 watts continuous Second the peak
    starting power of every A/C is the higher 19 amp (unless
    you've added a "soft start" to the A/C) Third, there are
    other draws, like the converter and fridge.

    Generally -with- a soft start the min generator is 2200
    watts, without 3KW (I prefer two ~2KW as I can carry them)

    Thanks, Ralph (and to George and sticks for similar advice).

    Regarding generator ratings, I've been checking both peak and
    static specs; for example, the Westinghouse unit I linked
    earlier is stated as 1800/2500, so I'd think that might do it.

    In any case, I'm thinking I may just try that Westinghouse iGen
    2550DFc, and if it doesn't work then add a soft start.

    So here's an update. I went by Menard's yesterday just to look at
    what they had, and it just so happened that they had in stock the
    Westinghouse unit (and no others of similar capacity). Taking
    that as a sign it was meant to be, I went ahead and bought it.

    Now a bit of dumbassery. After adding oil and fuel, I could *not*
    get it to start--despite *many* yanks on the cord. I pulled the
    spark plug to see if I'd flooded it, but it seemed fine. Finally
    it occurred to me that the red light on the control panel might
    mean something. It was the oil light, and when I added more oil
    the unit started right up. In fairness, the dipstick goes in
    almost horizontally, so it's hard to read. Plus the manual had
    many warnings not to overfill.

    I took it to the trailer this afternoon, and it does indeed put
    out enough power to charge the battery. On the other hand, when I
    tried running the AC (with pretty much everything else off) the
    overload protection cut in. So I guess if I want to run the AC
    I'll need to try a soft start thingy.

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to sticks on Tue Aug 13 21:21:28 2024
    On Mon, 12 Aug 2024 19:30:46 -0500,
    sticks <[email protected]> wrote:
    On 8/12/2024 7:37 AM, Ted Heise wrote:
    FWIW, I could run the fridge on propane, but am not sure what
    you mean by "convertor."

    Your unit has a "45 Amp Converter/Loadcenter" which I assume is
    what charges your house batteries when plugged into AC.

    Oh that makes sense, thanks. But I think it's 30 Amps.

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to sticks on Wed Aug 14 13:02:46 2024
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to charge
    the battery. On the other hand, when I tried running the AC
    (with pretty much everything else off) the overload protection
    cut in. So I guess if I want to run the AC I'll need to try a
    soft start thingy.

    Yur makin' progress.

    Looking forward to finding out if the soft start works for you.
    I personally don't know anyone who uses one because of all
    having bigger generators.

    Well, it occurred to me last night that I'd run the unit only in
    Eco mode. My assumption is it wouldn't be any different in full/
    standard mode because the gen adapts to the load when in Eco, but
    it's no big deal to just try it in standard mode. I doubt it'll
    matter, but maybe I'll be pleasantly surprised.


    BTW, I can see where they (soft start) might come in handy at
    various camping joints. Some of them have 20/30 amp sites.
    Not sure exactly what they mean by that. I'm assuming the
    choice of either a regular 110 volt 20 amp plug or the rounded
    30 amp plug. I can see where lots of people need 110, but not
    a 30 amp service, so it makes sense. But, if the thing
    actually works, in a pinch you could stay at a site that only
    had the 20 amp service and still use it for your AC.

    Okay, I'm not quite getting this. One thing I don't think I've
    posted is that the AC will run when I have the trailer in my
    driveway and plugged in to a 110 V outlet. I think it may be a 20
    A circuit. Tripped the GFCI a time or two, and melted the plug on
    an extension cord that was not heavy enough gauge, but after
    getting a heavier duty cord it seems to run fine.

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From bfh@21:1/5 to Ted Heise on Wed Aug 14 12:05:25 2024
    Ted Heise wrote:
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to charge
    the battery. On the other hand, when I tried running the AC
    (with pretty much everything else off) the overload protection
    cut in. So I guess if I want to run the AC I'll need to try a
    soft start thingy.

    Yur makin' progress.

    Looking forward to finding out if the soft start works for you.
    I personally don't know anyone who uses one because of all
    having bigger generators.

    Well, it occurred to me last night that I'd run the unit only in
    Eco mode. My assumption is it wouldn't be any different in full/
    standard mode because the gen adapts to the load when in Eco, but
    it's no big deal to just try it in standard mode. I doubt it'll
    matter, but maybe I'll be pleasantly surprised.


    BTW, I can see where they (soft start) might come in handy at
    various camping joints. Some of them have 20/30 amp sites.
    Not sure exactly what they mean by that. I'm assuming the
    choice of either a regular 110 volt 20 amp plug or the rounded
    30 amp plug. I can see where lots of people need 110, but not
    a 30 amp service, so it makes sense. But, if the thing
    actually works, in a pinch you could stay at a site that only
    had the 20 amp service and still use it for your AC.

    Okay, I'm not quite getting this. One thing I don't think I've
    posted is that the AC will run when I have the trailer in my
    driveway and plugged in to a 110 V outlet. I think it may be a 20
    A circuit. Tripped the GFCI a time or two, and melted the plug on
    an extension cord that was not heavy enough gauge, but after
    getting a heavier duty cord it seems to run fine.

    I don't know how closely you're watching your watts and doing your
    PIE, but it's not 110 V anymore - it's 120.....................most places..............more or less.

    --
    bill
    Theory don't mean squat if it don't work.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From George Anthony@21:1/5 to sticks on Wed Aug 14 12:27:28 2024
    On 8/13/2024 4:52 PM, sticks wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    So here's an update.  I went by Menard's yesterday just to look at
    what they had, and it just so happened that they had in stock the
    Westinghouse unit (and no others of similar capacity).  Taking
    that as a sign it was meant to be, I went ahead and bought it.

    Now a bit of dumbassery.  After adding oil and fuel, I could *not*
    get it to start--despite *many* yanks on the cord.  I pulled the
    spark plug to see if I'd flooded it, but it seemed fine.  Finally
    it occurred to me that the red light on the control panel might
    mean something.  It was the oil light, and when I added more oil
    the unit started right up.  In fairness, the dipstick goes in
    almost horizontally, so it's hard to read.  Plus the manual had
    many warnings not to overfill.

    I took it to the trailer this afternoon, and it does indeed put
    out enough power to charge the battery.  On the other hand, when I
    tried running the AC (with pretty much everything else off) the
    overload protection cut in.  So I guess if I want to run the AC
    I'll need to try a soft start thingy.

    Yur makin' progress.
    Looking forward to finding out if the soft start works for you.  I personally don't know anyone who uses one because of all having bigger generators.

    BTW, I can see where they (soft start) might come in handy at various
    camping joints.  Some of them have 20/30 amp sites.  Not sure exactly
    what they mean by that.  I'm assuming the choice of either a regular 110 volt 20 amp plug or the rounded 30 amp plug.  I can see where lots of
    people need 110, but not a 30 amp service, so it makes sense.  But, if
    the thing actually works, in a pinch you could stay at a site that only
    had the 20 amp service and still use it for your AC.


    Most all campgrounds have separate 50 amp, 30 amp and 120v outlets. Not
    all have 50 amp but unless the campground is older than dirt, it will
    have 30amp.
    --
    “The Party told you to reject the evidence of your eyes and ears..."
    George Orwell

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From George Anthony@21:1/5 to Ted Heise on Wed Aug 14 12:32:13 2024
    On 8/14/2024 8:02 AM, Ted Heise wrote:
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to charge
    the battery. On the other hand, when I tried running the AC
    (with pretty much everything else off) the overload protection
    cut in. So I guess if I want to run the AC I'll need to try a
    soft start thingy.

    Yur makin' progress.

    Looking forward to finding out if the soft start works for you.
    I personally don't know anyone who uses one because of all
    having bigger generators.

    Well, it occurred to me last night that I'd run the unit only in
    Eco mode. My assumption is it wouldn't be any different in full/
    standard mode because the gen adapts to the load when in Eco, but
    it's no big deal to just try it in standard mode. I doubt it'll
    matter, but maybe I'll be pleasantly surprised.


    BTW, I can see where they (soft start) might come in handy at
    various camping joints. Some of them have 20/30 amp sites.
    Not sure exactly what they mean by that. I'm assuming the
    choice of either a regular 110 volt 20 amp plug or the rounded
    30 amp plug. I can see where lots of people need 110, but not
    a 30 amp service, so it makes sense. But, if the thing
    actually works, in a pinch you could stay at a site that only
    had the 20 amp service and still use it for your AC.

    Okay, I'm not quite getting this. One thing I don't think I've
    posted is that the AC will run when I have the trailer in my
    driveway and plugged in to a 110 V outlet. I think it may be a 20
    A circuit. Tripped the GFCI a time or two, and melted the plug on
    an extension cord that was not heavy enough gauge, but after
    getting a heavier duty cord it seems to run fine.


    You will need that heavier extension depending on the length. I run one
    of my ACs on a 15amp circuit at home pretty often. However, at 90+ deg
    F, it will trip the breaker. If I really need AC on super hot days, I
    just run the generator <grin>.
    --
    “The Party told you to reject the evidence of your eyes and ears..."
    George Orwell

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From George Anthony@21:1/5 to George Anthony on Wed Aug 14 12:36:29 2024
    On 8/14/2024 12:27 PM, George Anthony wrote:
    On 8/13/2024 4:52 PM, sticks wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    So here's an update.  I went by Menard's yesterday just to look at
    what they had, and it just so happened that they had in stock the
    Westinghouse unit (and no others of similar capacity).  Taking
    that as a sign it was meant to be, I went ahead and bought it.

    Now a bit of dumbassery.  After adding oil and fuel, I could *not*
    get it to start--despite *many* yanks on the cord.  I pulled the
    spark plug to see if I'd flooded it, but it seemed fine.  Finally
    it occurred to me that the red light on the control panel might
    mean something.  It was the oil light, and when I added more oil
    the unit started right up.  In fairness, the dipstick goes in
    almost horizontally, so it's hard to read.  Plus the manual had
    many warnings not to overfill.

    I took it to the trailer this afternoon, and it does indeed put
    out enough power to charge the battery.  On the other hand, when I
    tried running the AC (with pretty much everything else off) the
    overload protection cut in.  So I guess if I want to run the AC
    I'll need to try a soft start thingy.

    Yur makin' progress.
    Looking forward to finding out if the soft start works for you.  I
    personally don't know anyone who uses one because of all having bigger
    generators.

    BTW, I can see where they (soft start) might come in handy at various
    camping joints.  Some of them have 20/30 amp sites.  Not sure exactly
    what they mean by that.  I'm assuming the choice of either a regular
    110 volt 20 amp plug or the rounded 30 amp plug.  I can see where lots
    of people need 110, but not a 30 amp service, so it makes sense.  But,
    if the thing actually works, in a pinch you could stay at a site that
    only had the 20 amp service and still use it for your AC.


    Most all campgrounds have separate 50 amp, 30 amp and 120v outlets. Not
    all have 50 amp but unless the campground is older than dirt, it will
    have 30amp.

    I know they are all 120 volt (i.e., on each leg). I meant 20 amps.
    --
    “The Party told you to reject the evidence of your eyes and ears..."
    George Orwell

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Mike Van Pelt@21:1/5 to [email protected] on Wed Aug 14 19:07:30 2024
    In article <v9ipms$hn7m$[email protected]>,
    George Anthony <[email protected]> wrote:
    You will need that heavier extension depending on the length. I run one
    of my ACs on a 15amp circuit at home pretty often. However, at 90+ deg
    F, it will trip the breaker. If I really need AC on super hot days, I
    just run the generator <grin>.

    Also, a long not-heavy-enough extension cord will have a voltage
    drop. My WatchDog sometimes trips due to the voltage hitting 104.
    --
    Mike Van Pelt | "I don't advise it unless you're nuts."
    mvp at calweb.com | -- Ray Wilkinson, after riding out Hurricane
    KE6BVH | Ike on Surfside Beach in Galveston

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From George Anthony@21:1/5 to Mike Van Pelt on Wed Aug 14 14:19:42 2024
    On 8/14/2024 2:07 PM, Mike Van Pelt wrote:
    In article <v9ipms$hn7m$[email protected]>,
    George Anthony <[email protected]> wrote:
    You will need that heavier extension depending on the length. I run one
    of my ACs on a 15amp circuit at home pretty often. However, at 90+ deg
    F, it will trip the breaker. If I really need AC on super hot days, I
    just run the generator <grin>.

    Also, a long not-heavy-enough extension cord will have a voltage
    drop. My WatchDog sometimes trips due to the voltage hitting 104.

    True. And another reason is high ambient temperatures will cause
    breakers to trip. High temperatures also increase the voltage drop.
    --
    “The Party told you to reject the evidence of your eyes and ears..."
    George Orwell

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to Ted Heise on Thu Aug 15 01:05:56 2024
    On Wed, 14 Aug 2024 13:02:46 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to charge
    the battery. On the other hand, when I tried running the AC
    (with pretty much everything else off) the overload
    protection cut in. So I guess if I want to run the AC I'll
    need to try a soft start thingy.

    Yur makin' progress.

    Didn't say it before, but I appreciate the encouraging words.


    Looking forward to finding out if the soft start works for
    you. I personally don't know anyone who uses one because of
    all having bigger generators.

    As I'll explain below, I may have to go that way. Problem is I
    would hate to go to the trouble and expense and have it not work.
    I wonder if the soft start company someone linked could give me a
    guess on how likely it is to work.


    Well, it occurred to me last night that I'd run the unit only
    in Eco mode. My assumption is it wouldn't be any different in
    full/ standard mode because the gen adapts to the load when in
    Eco, but it's no big deal to just try it in standard mode. I
    doubt it'll matter, but maybe I'll be pleasantly surprised.

    So the non-Eco mode did the same thing as the Eco mode--tripped
    the generator's overload almost immediately. I also tried
    starting with just the AC fan, then adding the cooling (as
    suggested in a privagte message), but no joy.

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to Ted Heise on Tue Aug 20 01:00:31 2024
    On Thu, 15 Aug 2024 01:05:56 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Wed, 14 Aug 2024 13:02:46 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to
    charge the battery. On the other hand, when I tried
    running the AC (with pretty much everything else off) the
    overload protection cut in. So I guess if I want to run
    the AC I'll need to try a soft start thingy.

    Looking forward to finding out if the soft start works for
    you. I personally don't know anyone who uses one because
    of all having bigger generators.

    As I'll explain below, I may have to go that way. Problem is I
    would hate to go to the trouble and expense and have it not
    work. I wonder if the soft start company someone linked could
    give me a guess on how likely it is to work.

    Okay, here's an update. Yesterday I climbed up top of the trailer
    and accessed the wiring compartment of the AC, finding the wiring
    diagram approximately where the SoftStartRV website said it would
    be. I sent an inquiry to them with the AC and generator specs and
    got a reply promptly this morning that sounded confident it would
    work for me. So I went ahead and ordered it, should be here later
    this week. I try installing it this weekend <gulp> and let you
    all know what happens.

    Planning a trip to the Ozarks in early Oct, and may well not even
    need the AC. Heh.

    --
    Ted Heise <[email protected]> West Lafayette, IN, USA

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From bfh@21:1/5 to Ted Heise on Mon Aug 19 22:18:47 2024
    Ted Heise wrote:
    On Thu, 15 Aug 2024 01:05:56 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Wed, 14 Aug 2024 13:02:46 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to
    charge the battery. On the other hand, when I tried
    running the AC (with pretty much everything else off) the
    overload protection cut in. So I guess if I want to run
    the AC I'll need to try a soft start thingy.

    Looking forward to finding out if the soft start works for
    you. I personally don't know anyone who uses one because
    of all having bigger generators.

    As I'll explain below, I may have to go that way. Problem is I
    would hate to go to the trouble and expense and have it not
    work. I wonder if the soft start company someone linked could
    give me a guess on how likely it is to work.

    Okay, here's an update. Yesterday I climbed up top of the trailer
    and accessed the wiring compartment of the AC, finding the wiring
    diagram approximately where the SoftStartRV website said it would
    be. I sent an inquiry to them with the AC and generator specs and
    got a reply promptly this morning that sounded confident it would
    work for me. So I went ahead and ordered it, should be here later
    this week. I try installing it this weekend <gulp> and let you
    all know what happens.

    Planning a trip to the Ozarks in early Oct, and may well not even
    need the AC. Heh.

    Hey. Look at the bright side - you'll have all of late fall, winter,
    and early spring to work on the problem.

    --
    bill
    Theory don't mean squat if it don't work.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Ted Heise@21:1/5 to bfh on Wed Aug 21 17:28:57 2024
    On Mon, 19 Aug 2024 22:18:47 -0400,
    bfh <[email protected]> wrote:
    Ted Heise wrote:
    On Thu, 15 Aug 2024 01:05:56 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Wed, 14 Aug 2024 13:02:46 -0000 (UTC),
    Ted Heise <[email protected]> wrote:
    On Tue, 13 Aug 2024 16:52:59 -0500,
    sticks <[email protected]> wrote:
    On 8/13/2024 4:30 PM, Ted Heise wrote:

    I took it [Westinghouse iGen 2550] to the trailer this
    afternoon, and it does indeed put out enough power to
    charge the battery. On the other hand, when I tried
    running the AC (with pretty much everything else off) the
    overload protection cut in. So I guess if I want to run
    the AC I'll need to try a soft start thingy.

    Looking forward to finding out if the soft start works
    for you. I personally don't know anyone who uses one
    because of all having bigger generators.

    As I'll explain below, I may have to go that way. Problem
    is I would hate to go to the trouble and expense and have
    it not work. I wonder if the soft start company someone
    linked could give me a guess on how likely it is to work.

    Okay, here's an update. Yesterday I climbed up top of the
    trailer and accessed the wiring compartment of the AC, finding
    the wiring diagram approximately where the SoftStartRV website
    said it would be. I sent an inquiry to them with the AC and
    generator specs and got a reply promptly this morning that
    sounded confident it would work for me. So I went ahead and
    ordered it, should be here later this week. I try installing
    it this weekend <gulp> and let you all know what happens.

    Planning a trip to the Ozarks in early Oct, and may well not
    even need the AC. Heh.

    Hey. Look at the bright side - you'll have all of late fall,
    winter, and early spring to work on the problem.

    LOL. Good point, thx!

    --